How much full load real power in kilowatts does a three-phase generator with a terminal voltage of 600 V and a current of 200 A at 80% power factor deliver?

Study for the 3rd Class Power Engineering (3A2) Exam. Explore multiple choice questions with hints and explanations. Prepare for your certification!

To find the full load real power delivered by a three-phase generator, the formula used for calculating real power (P) in kilowatts is:

[ P (kW) = \sqrt{3} \times V \times I \times \text{Power Factor} ]

Where:

  • ( V ) is the line-to-line voltage in volts

  • ( I ) is the current in amperes

  • The power factor accounts for the phase difference between the voltage and current.

In this case:

  • The terminal voltage ( V = 600 , \text{V} )

  • The current ( I = 200 , \text{A} )

  • The power factor = 0.80 (which is 80%)

Plugging in these values:

  1. Calculate the full load real power using the formula:

[ P = \sqrt{3} \times 600 \times 200 \times 0.80 ]

Calculating step-by-step:

  • First, calculate ( \sqrt{3} ) (approximately 1.732).

  • Then, multiply:

  • ( 600 \times 200 = 120,000 )

  • Then, multiply by the