At what voltage does a three-phase generator operate if it delivers 220 A with a power factor of 0.8 and the real power output is calculated to be 166.08 kW?

Study for the 3rd Class Power Engineering (3A2) Exam. Explore multiple choice questions with hints and explanations. Prepare for your certification!

To determine the operating voltage of the three-phase generator, we can utilize the formula for real power in a three-phase system:

[ P = \sqrt{3} \times V \times I \times \text{PF} ]

Where:

  • ( P ) is the real power in watts (W),

  • ( V ) is the line-to-line voltage in volts (V),

  • ( I ) is the current in amperes (A),

  • ( \text{PF} ) is the power factor (a unitless number between 0 and 1).

Given that the real power output ( P ) is 166.08 kW, we first convert that to watts:

[ 166.08 , \text{kW} = 166080 , \text{W} ]

The current ( I ) is given as 220 A, and the power factor ( \text{PF} ) is 0.8. We need to solve for ( V ):

  1. Rearranging the formula to solve for ( V ):

[ V = \frac{P}{\sqrt{3} \times I \times \text{PF}} ]

2