A three-phase generator delivers current at a power factor of 75% with a terminal voltage of 480 V and a full load current of 300 A. What is the apparent power?

Study for the 3rd Class Power Engineering (3A2) Exam. Explore multiple choice questions with hints and explanations. Prepare for your certification!

To determine the apparent power delivered by the three-phase generator, we can use the formula for apparent power in a three-phase system, which is given by:

[

S = \sqrt{3} \times V_L \times I

]

Where:

  • ( S ) is the apparent power in VA (or kVA when divided by 1000),

  • ( V_L ) is the line-to-line voltage in volts,

  • ( I ) is the current in amperes.

In this situation, the terminal voltage is provided as 480 V, and the full load current is 300 A. Plugging these values into the formula gives:

[

S = \sqrt{3} \times 480 , V \times 300 , A

]

Calculating this step-by-step:

  1. Calculate ( \sqrt{3} ): Approximately ( 1.732 ).

  2. Multiply ( 1.732 ) by ( 480 ):

[

1.732 \times 480 \approx 829.76 , V

]

  1. Now, multiply this result by ( 300 ):

[

829.76 \